Hola jherson; Los participantes en este foro de Siemens vienen de numerosos países y todos no hablan español. Para facilitar el acceso a las preguntas y respuestas, hemos decidido usar inglés como idioma de intercambio. Haznos el favor de escribirnos en inglés a la próxima visita . Hello jherson; Participants in the Siemens forum come from many countries, and not all speak Spanish. To facilitate access to questions and answers, we have chosen English as an international language. Please do us the favor of writing in English on your next visit. Now, to read values from the drive and transfer them to a Profibus telegram, you must reserve supplemental PZD words, for example PPO5 will give you 8 extra words to exchange values (study the screenshot you posted earlier). Next you must assign the parameters (power, current, voltage...) you want to read to these PZD words. The following application example will show you how: MM4, G120/G120D (CU2x0x): Which parameters can be read-out using PZD? https://support.industry.siemens.com/cs/us/en/view/23642364 Hope this helps, Daniel Chartier |