10/21/2009 6:39 PM | |
Joined: 5/13/2008 Last visit: 12/18/2019 Posts: 836 Rating: (71) |
Hi mohajer, do we talking about the RT? If so, please see further instructions at this FAQ: http://support.automation.siemens.com/WW/view/en/32813726 You may use the methode as descriped in table2, but the ini-file is not configured right. |
mfG / Best regards |
|
7/31/2014 1:29 PM | |
Posts: 2 Rating: (7) |
Hello all I have answear from Technical Support Germany Tech Supportwrites: Please do the following: 1. Please restart your PC. 2. Please delete the "Default layout.xml" in the following path: C:\Documents and Settings\<LoginName>\AppData\Roaming\SIEMENS AG\SIMATIC WinCC flexible 2008\Caches\1.4.0.3_105.9\Documentation\Settings\Default layout.xml After this please copy the "Default layout.xml" under attachments of this mail in this path. In my case it works AttachmentDefault layout.zip (2076 Downloads) |
Last edited by: CS Moderator at: 7/31/2014 1:35 PMpersonal Data edited |
|
This contribution was helpful to13 thankful Users |
4/23/2015 3:43 PM | |
Posts: 1 Rating: (0) |
It's work for me too. Thank you |
Last edited by: U_032f43cf-007f-4cb9-8b77-bafc6293354b at: 4/23/2015 3:45:05 PM |
|
7/23/2015 7:54 AM | |
Joined: 9/17/2012 Last visit: 10/18/2024 Posts: 1 Rating: (0) |
Worked for me as well |
1/15/2016 7:05 AM | |
Joined: 6/5/2011 Last visit: 11/16/2023 Posts: 2 Rating: (0) |
Thanks. Worked. :) |
10/13/2016 3:55 PM | |
Posts: 14 Rating: (1) |
Worked for my I have: 2008 SP2 upd10 running Xp SP3 |