2/24/2025 2:02 PM | |
Joined: 10/5/2020 Last visit: 3/10/2025 Posts: 11 Rating:
|
Hi all, what is desired method of doing hardwired safety signal exchange for PLd? Intentionally, I'd like to have it hardwired, not exchanged via network (F-Link etc). Lets determine the conditions: - 2x S7-1500F CPU - each CPU connected to its own ET200SP with FDI (6ES7136-6BA01-0CA0) and FDO (6ES7136-6DB00-0CA0) modules - each ET200SP has E-Stop connected as presented in (https://support.industry.siemens.com/cs/document/21064024/emergency-stop-up-to-sil-3-pl-e-with-a-fail-safe-s7-1500-controller-?dti=0&lc=en-PL) so it's 2x NC channels with 1oo2 evaluation in FDI FDO manual presents a method to output PLe signal in single channel in Cat.4 . FDI manual presents how to connect single channel as PLd Cat.3. We all know that Cat.3 and Cat.4 require dual channel architecture, so I find it a bit dusty. That's why I doubt about the correct way to exchange E-Stop bit between PLC's. Shall it be 1x FDI - 1x FDO, 2x FDI - 2x FDO or maybe other configuration? I came across this topic (https://support.industry.siemens.com/forum/pl/en/posts/cat-3-with-single-channel-input/34167) and it makes a little bit sense that 1oo2 evaluation should be done in software when its not done in hardware, but it's just a opinion not statement in the manual. Does anyone knows the answer |
3/10/2025 8:02 AM | |
Joined: 10/5/2020 Last visit: 3/10/2025 Posts: 11 Rating:
|
Bump |