Joined: 3/17/2017 Last visit: 7/26/2024 Posts: 13 Rating: (0) |
hi I need to connect two plc logo 8.3 to a hmi ktp400basic panel can you help me configure the tsap ports Thank you |
2/4/2023 1:56 PM | |
Joined: 12/18/2014 Last visit: 9/24/2024 Posts: 33833 Rating: (4205)
|
Here's an example with TIA V14 SP1. You don't need to make a connection in the LSC, only in TIA. Then is the HMI the client and the LOGO!s are the servers. Attachmenttoni66.zip (494 Downloads) |
2/5/2023 7:50 AM | |
Joined: 3/17/2017 Last visit: 7/26/2024 Posts: 13 Rating: (0) |
Thanks for replying, tia portal version V13 TWO logo 6ED1052-1MD08-0BA1 |
2/5/2023 8:07 AM | |
Joined: 3/17/2017 Last visit: 7/26/2024 Posts: 13 Rating: (0) |
SEND NETWORK PROJECT IMAGE |
2/5/2023 8:19 AM | |
Joined: 12/18/2014 Last visit: 9/24/2024 Posts: 33833 Rating: (4205)
|
As I wrote, you don't need to make any connection in LSC to the HMI. You must only create for every LOGO! a own connection TIA. Here's a version with TIA V13 SP2 Update 4. Attachmenttoni66.zip (462 Downloads) |
2/5/2023 10:47 AM | |
Joined: 3/17/2017 Last visit: 7/26/2024 Posts: 13 Rating: (0) |
thank you very much I take advantage of your kindness and experience I enclose the project
AttachmentPALASPORT 05-02-2023-4.zip (514 Downloads) |