1/26/2023 8:38 PM | |
Joined: 3/3/2021 Last visit: 2/22/2024 Posts: 16 Rating: (0) |
Thsnk you for reply .. I want this change time with LOGO .. |
1/26/2023 10:41 PM | |
Joined: 6/11/2019 Last visit: 4/23/2024 Posts: 2176 Rating: (95) |
Hello ALMOHARG, I can think of two options. With one, the input is evaluated and the display shows whether you are outside the input window. If this is the case, the triggering of the time relay is interrupted (sample 1). With the other option, the time is converted via inputs (e.g. logo button UP and Down). This variant can be supplemented with a "Push and Hold" (Sample 2). In both variants, the time is entered on the time basis of the delay module (e.g. 1 minute and 30 seconds are then 90 seconds) Kind regards Ella_68 (translated with Google) AttachmentSchaltplan1.zip (305 Downloads) |
This contribution was helpful to1 thankful Users |
1/27/2023 2:50 AM | |
Joined: 12/18/2014 Last visit: 4/23/2024 Posts: 32871 Rating: (4064)
|
Here's another possible solution.
AttachmentStore_only_accepted_values_0BA8.Standard.zip (318 Downloads) |
1/27/2023 7:01 PM | |
Joined: 12/18/2014 Last visit: 4/23/2024 Posts: 32871 Rating: (4064)
|
Yes, you're right. But it is not a small, but a big bug. Here's the corrected version. AttachmentStore_only_accepted_values_0BA8.Standard_V2.zip (286 Downloads) |
This contribution was helpful to2 thankful Users |
Follow us on