Hi, how often do you want to send these data to your plc, every minute, hour, day or just once....? nemo |
4/20/2006 7:45 AM | |
Posts: 102 Rating: (9) |
Hi Thank you for your help. I have to send this information every 50 second. Thanks Mehrnoosh |
4/20/2006 8:19 AM | |
Posts: 3149 Rating: (171)
|
Hi Mehrnoosh, well, you should know, that using rawdata tags for this amount of data in such short time periods will cause a lot of communication load and certainly reduce dramaticly your WinCC permformance. => I can NOT recommend this http://support.automation.siemens.com/WW/view/en/21916098 The length of your rawdata is depending on your S7-CPU, please check this in the FAQ mentioned above and your WinCC help. => you should really check, whether it´s necessary to exchange so many data between S7 and your database... nemo |