Hi, Today I thought about comparing the hardware of the project with the online plc and I really didn't find any options, it's very strange, cause it would be interesting when we go online on the plc with tia portal at least one warning message popup to we know that hardware are different. Step 7 classic when we go online, show the popup warning. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 06/23/2022 10:21:38New subject after splitting |
|
6/23/2022 4:43 PM | |
Joined: 7/7/2010 Last visit: 7/12/2024 Posts: 14948 Rating: (2393)
|
I know of at least 2 ways. Easy way is to go online using online & diagnostics for main PLC. Review the diag buffer entries right after the PLC starts after a full plc hardware configuration download. Every module with different firmware or part # difference will insert an entry into the buffer. You can visit each module in the project, use the online & diagnostics option (right-click on each module is how I get there), and then see the firmware / part # differences from physical to configured hardware. If you want, you can configure the startup parameters to prevent startup for any differences, then review the RED X diag buffer entries for all the mismatched hardware. Is that what you mean? Yeah, Portal is kinda missing this. It's much easier to gather this information in Sinamics Starter software.
|
science guy |
|
This contribution was helpful to1 thankful Users |
6/28/2022 3:51 PM | |
Joined: 10/22/2015 Last visit: 6/7/2024 Posts: 23 Rating: (4) |
yes, but when you have safety PLC and Sinamics with PROFIsafe, you can't upload, it's too bad. |