Joined: 11/2/2021 Last visit: 5/28/2024 Posts: 2 Rating: (0) |
Hi, I have a similar problem I was able to connect to HART instrumentation equipment such as PROMAG53, through the HART modem with SIMATIC PDM (standalone) software, to observe and adjust its parameters. On the other hand, by the IM153-2 and its HART analog input module (6es7153-2ab02-0xb0,6es7331-7tf01-0ab0) , I was able to get its PV, SV, TV and QV of the instruments. But when I opened the PDM by double clicking on the hart field device which I entered below the analog input , I could not communicate with the desired hart equipment and could not upload to PG their hart parameter values. There can be a lot of instrumentation equipment in the field. I want to know if it is possible to communicate with hart instrumentations equipment which is connected to the hart analog input modules without using modem or hart handheld communicator through PCS7 software and PDM to config and diagnostic and change its hart parameter values? If so, how can it be done? ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 05/10/2022 13:30:05New subject after splitting |
|
5/31/2022 1:11 PM | |
Joined: 1/11/2019 Last visit: 9/10/2024 Posts: 758 Rating: (150)
|
Hello mhmdms, You can use below steps to configure and communicate the HART devices using PCS7 and PDM. Procedure for Hart Communication Via PDM mode 1. Install Simatic PCS7 & PDM Please find the attached (Steps_Snapshot.zip) for the configuration steps. kindly match the steps number with attached snapshots. I hope it helps you! AttachmentSteps Snapshot.zip (480 Downloads) |
This contribution was helpful to2 thankful Users |