I want to integrate Variable Air Volume (Zennio Minibox 0-10V X2) regulators in to the PXC001e.d. Basically, every Zennio regulator has two analog outputs 0-10V to which I have connected group addresses using ETS5 and I have already done download to the device using ETS tool. Next thing to do was to make bindings to PXC001e.d. using PX-KNX Tool - I have already done all of that successfully. Next thing to do was to add those datapoints to "Point configurator" in XWorks Plus and then to generate CFC. Problem for me is that I always see only one analog output in the CFC and for the other one there is error "Target object not known". If I try to make another PX-KNX Tool project adding only the analog output that previously didn't work, then I can read this output in the CFC - so it is not always the same output that doesn't work. You can see all of this in the attachment. Can somebody point me in the right direction - what could be the problem ? Best regards AttachmentProblem.docx (309 Downloads) |