Translation from the Spanish text
Hola SGAR; Este foro de Siemens atrae a participantes de muchos lugares, donde muchos no entienden el español. Para facilitar nuestros intercambios el el foro, hemos escogido al ingles como idioma internacional. Haznos el favor de excribir en ingles a tu próxima visita. Hello SGAR; This forum from Siemens brings together participants from mny places, where Spanish is not spoken. To make our exchanges easier in the forum, we have selectd English as an international language. Please write to us in English on your next visit. SFC12 (D_ACT_DP) is used to activate (and re-activate) configured Profinet IO devices (and DP slaves) from the user program. See section 16.3 in the System and Standard Functions manual: https://support.industry.siemens.com/cs/ca/en/view/1214574 An Ethernet switch is not configured (with its unique I/O address) as part of the Step 7 program, so it cannot be de-activated using SFC 12.. But you can individualy de-activate the IO Devices connected to that switch, if that can provide you.with a solution. Hope this helps, Daniel Chartier
|