HELLO, I have gone through your discussion, and I have question that Will PCA3200 support IM 151-1 series.????? Warm Regards Pallav Bhatt
Splitted from Sentron PAC3200 - i need read active energy . |
Last edited by: O_Moderator at: 7/6/2010 9:02 AMnew subject after splitting |
|
7/6/2010 8:58 AM | |
Joined: 5/28/2008 Last visit: 10/12/2024 Posts: 4515 Rating: (839) |
Hello, I cann't tell that I have understand your question well. But if you want to connect the PAC3200 device to a profibus network, then you have to buy the Sentron profibus module 7KM9300-0AB00-0AA0. And you have to mount it on the rear of the Sentron PAC3200 device. Hope this helps. |
Ayman Elotaify |
|
7/6/2010 12:33 PM | |
Posts: 433 Rating: (48) |
Hi, IM151-1 is a DP module. You can connect it with a dp module of PAC3200. The other possibility is to connect the PAC3200 via TCP. For PAC3200 you can use a TCP module as well. As CPU you can use IM151-8 (or another CPU) and OpenModbusTCP. Tomcat |