11/11/2010 10:39 PM | |
Joined: 11/11/2008 Last visit: 8/12/2022 Posts: 719 Rating: (62) |
Hello Rojas17 for more Information you can download the Manual. http://support.automation.siemens.com/WW/view/en/40786078 Best regards ring24h |
Antworten wären einfacher, wenn bei Anfragen die Logo! Version (0BAx, R?...) und die Spannung (12/24, 24, 230) angegeben würde |
|
11/12/2010 8:25 AM | |
Posts: 2930 Rating: (432)
|
Hi, LOGO! does not have PID. Only PI is available. Here you can download the LOGO!Soft Demo: https://www.automation.siemens.com/mcms/programmable-logic-controller/de/logikmodul-logo/demo-software/Seiten/Default.aspx?HTTPS=REDIR#Demosoftware A simualtion mode is inlcuded so you try and check. Analog Inputs: 1. Onboard up to 4, 0..10V, 1000 Steps resolution 2. Expansion module: AM2 0.. 10V or 0/4...20mA, 1000 steps resolution, 2 Inputs 3. Expansion module: AM2 RTD, -50 ....200°C, Pt100 or Pt1000, 1000 steps resolution, 2 Inputs Everything else you can find in the manual or the online help. Hope this helps |