1/20/2012 9:43 AM | |
Posts: 50 Rating: (6)
|
I think there is no mal function of the PAC meter. The working hour counter starts with the set value of current zero point suppression level. The zero point suppression level can be set via the interface in the range 0% to 10% of the measuring range final value (default value 0.0%). Currents within this range are indicated on the display with "0" (zero). |
1/25/2012 5:16 AM | |
Posts: 262 Rating: (45) |
Hi, Refer the screen shot of Powerconfig2.2, use the setting to avoid the problem of wrong reading in work counter. In future also, it is advisble to use powerconfig software to parameterise PAC / 3WL devices. AttachmentPresentation1.zip (275 Downloads) |