6/3/2014 4:49 PM | |
Posts: 14 Rating: (0) |
Dear all. I wonder if the repair 3RT1945-5AN21 COIL FOR Contactors is suitable for contactor 3RT1647 1AN21-capacitor AC CONTACTOR SW-6. tks. |
6/5/2014 8:17 PM | |
Posts: 14 Rating: (0) |
no fix for the contactor 3RT1647 1AN21? the manual says nothing about it. You can indicate which coil repair? tks. |
6/6/2014 2:12 PM | |
Posts: 14 Rating: (0) |
in the manual that I have, does not have information on coil. but need the order code. can you pass me the manual also. |
6/6/2014 2:39 PM | |
Joined: 1/21/2013 Last visit: 3/19/2024 Posts: 4618 Rating: (705) |
Hello rafael-ws, Your coil code is not correct, you need 3RT1944-5AN21 220V,50Hz for 3RT1647 and the coil for 230V,50Hz if you want is 3RT1944-5AL21 I have in front of me the printed manual LV 2006 that can not find with google, if you wait a while I try to find it. Have a look: 3RT16 Capacitor contactors - Coil replacement - Siemens Industry ... |
Last edited by: Ste39 at: 6/6/2014 3:58 PMLast edited by: Ste39 at: 6/6/2014 3:55 PMLast edited by: Ste39 at: 6/6/2014 2:41 PM |
|