Dear all,
I am facing problem when I try to open old STEP 7 backup from simatic manager V5.5. I attached all the screen shots, I have not installed simotion scout or starter software but I downloaded S120 GSD file from support site & installed, after installation also still I am getting same GSD file missing popup, Dear Experts please help me to find the solution for this problem. With Regards, Dhinagaran. V AttachmentGSD_pbm_imag.zip (38 Downloads) |
2/1/2016 6:39 AM | |
Joined: 5/12/2006 Last visit: 5/2/2024 Posts: 22243 Rating: (2981) |
Hello, the problem is that the SINAMICS drive in the project is not created with a GSD / GSDML File. The Sinamics Device is created with the catalog data which is installed with So you must install Scout or Starter to work correctly with the project. The latest Starter Version you can download here: https://support.industry.siemens.com/cs/ww/en/view/26233208 Regards |