7/5/2018 4:31 PM | |||||||||||||||||
Joined: 9/8/2010 Last visit: 12/27/2023 Posts: 45 Rating:
Hi I am facing a problem with S7 1500 Analog module (6ES7 531-7KF00-0AB0) that peripheral input gives 50% Value(13603 Counts) for 4mA and It gives 100% value(27648 counts which is over range) for 8mA also find the table below for other ranges. these tests done by injecting mA and by isolated instruments.
Kindly advise me on this problem as soon as possible. Thanks Prabu AttachmentConfig.zip (311 Downloads) |
7/17/2018 6:58 PM | |
Hi all, finally solved, thanks for your support. It become ok after download HW configuration,restart the PLC. Thanks and Regards Prabu |