Hi All, I have encountered some issues with downloading a FB in a siemens s7 1500 PLC A PLC(516-3an01-0ab0) in our factory broke down so this was replaced with a new one. We received a backup of the project file (Tia V13). I made some improvements in the program but when I try to download this I got the following message (see image), that there is a difference in the firmware version (2.5 online vs 1.8 offline). How can I update the firmware of the CPU in the offline project? I have downloaded the following package: (but I cannot import it in tia v13 trough "Options > Support Packages", because this is an .upd file) https://support.industry.siemens.com/cs/de/en/view/109478459 I also downloaded the following package: (But I do not now which one to import this in tia, and it is unclear for me if this contains the right firmware) https://support.industry.siemens.com/cs/ww/en/view/72341852 Besides I have another question: Can I have a conflict if it is reversed. So for example, I have an online firmware of 1.8 but an offline version of 2.5, do I get conflicts? or do I have to downgrade the offline version? |
Last edited by: Jen_Moderator at: 11/22/2018 2:08:08 PMOptimized links. |
|
This contribution was helpful to1 thankful Users |
11/22/2018 1:38 PM | |
Joined: 8/31/2005 Last visit: 6/14/2024 Posts: 2198 Rating: (328) |
HSP - Hardware Support Package Firmware A CPU with newer firmware as programmed, will work like a CPU with the programmed firmware. A download of a programmed newer firmware version in a CPU with older firmware is not possible. |
|
|