10/6/2016 12:11 PM | |
Joined: 11/14/2008 Last visit: 5/6/2024 Posts: 504 Rating: (22) |
Hi, Maybe this post can help you further. it's same device and also problem finding gsd. In this FAQ you can find back example on Measuring and Visualizing Energy Data |
Last edited by: OmegaProjects at: 10/6/2016 12:12:16 PM |
|
10/6/2016 2:14 PM | |
Joined: 9/27/2006 Last visit: 6/14/2024 Posts: 12260 Rating: (2671) |
Hello drozerce; The gsd file you are pointing to is for the Profinet expansion module for the PAC family. You need a 7KM PAC Profibus-DP expansion module in the PAC 3200 to enable it as a Profibus slave. Once you have it you can dowload the appropriate gsd file and manual from the links below: - 7KM9300-0AB01-0AA0 PROFIBUS DP expansion module PROFIBUS DP expansion module, plug-in, for 7KM PAC3200 / 4200 / 3VA COM100 / 800 - GSD files - Expansion module PAC PROFIBUS DP, 7KM9300-0AB01-0AA0https://support.industry.siemens.com/cs/om/en/view/84054777 Download the GSD_PAC3200_V40.zip file - Manual 7KM PAC Profibus DP, 7KM SWITCHED ETHERNET expansion modules https://support.industry.siemens.com/cs/fr/en/view/26504372 Hope this helps, Daniel Chartier |
10/6/2016 2:57 PM | |
Joined: 5/12/2006 Last visit: 6/14/2024 Posts: 22263 Rating: (2989) |
Hello, yes is it. And for thios modules you can download the PROFINET GSDML Files (https://support.industry.siemens.com/cs/ww/en/view/59840946) Then in the catalog is the Ordernumber of the Expansion module and not from the PAC3200 that is correct. Regards Christoph |
This contribution was helpful to1 thankful Users |