Hi Sundar babu I think your post should be in Decentral Peripherie to get more help to the topic. |
Best Regards |
|
4/12/2016 10:04 PM | |
Joined: 10/2/2013 Last visit: 9/30/2024 Posts: 339 Rating: (52) |
Dear sundar Babu, Please refer below link it may help you, https://support.industry.siemens.com/tf/ww/en/postattachments/download/?attachmentId=16829 |
Technology is best when it brings people together,so we are here now :) |
|
4/15/2016 3:56 AM | |
Posts: 39 Rating: (0) |
Experts have any solution for my query???? |
4/17/2016 5:02 PM | |
Joined: 7/2/2008 Last visit: 9/30/2024 Posts: 928 Rating: (308) |
Hello Sundar, I'm sorry I didn't notice your reply (Automatic notification was not ON). I've been "quickly" through your project. You assigned all IOs to OB1 PI. It will work but it's highly recommended to assign redundant IOs to PIPs assigned to cyclic interrupts (OB3X). It's also a bit strange to configure couple of redundant channels and leave the rest. It should work but a bit strange. Now, I can see in OB1 that you are moving PIW598 to MW100. You should know that redundant IOs work with process image addressing not peripheral addressing. So, you should use IW 298 not PIW298. I recommend to have a look on this PCS7 document for some guidance on how to assign PIPs and how to configure redundant IOs. Best regards, H-H |
Last edited by: H-H at: 4/17/2016 5:09:31 PMMissing link |
|