(0)| 8/9/2023 1:09 PM | |
|
Joined: 9/27/2006 Last visit: 1/16/2026 Posts: 12481 Rating:
|
Hello CoreGuy; Based on the pdf doumentation file that accpanies ths article redundant OPC UA servers must be configured with different URLs and PC names.
https://support.industry.siemens.com/cs/do/en/view/99923489 Note however that the article details the requirements for redundant OPC UA servers on a WinCC Advanced system, you will have to give us more details on your present installation if you would require more help. Hope this helps, Daniel Chartier |
This contribution was helpful to
|
|
| 8/15/2023 12:41 AM | |
|
Joined: 9/9/2015 Last visit: 12/5/2025 Posts: 732 Rating:
|
I have two cases study for you 1. With the redundant WinCC , we install KepServerEx or Cogent Datahub Redundancy in a dedicated OPC station and connect to all the WinCC for data sharing. 2. In PCS 7 WinCC environment, we install OpenPCS 7 in dedicated OPC Station for data sharing with redundancy functionality. |
|
Please give me 5 stars Rating if my post is helpful for you. :) |
|