Hello Ehsan.nami, Have you taken the following into account? |
|
If this Information really helps, you could use the Rate function |
|
| 9/29/2023 10:42 AM | |
|
Joined: 8/3/2009 Last visit: 1/19/2026 Posts: 16644 Rating:
|
Hello Ehsan.nami Which Version of WInCC do you use exactly? Which FW Version of the PLC do you use exactly? If you use < WinCC V7.5SP2 Upd4 then you have to deactivate the secure HMI communication in the PLC (if you have a newer FW) if you have a newer Version then look at this FAQ: https://support.industry.siemens.com/cs/de/en/view/109798498 Check also your access point in the WInCC Channel and/or set the PGPC Interface to the correct setting Bye Murof |
Last edited by: Murof at: 09/29/2023 10:43:19If this Information really helps, you could use the Rate function |
|
This contribution was helpful to
|
|
| 10/4/2023 8:10 AM | |
|
Joined: 9/27/2014 Last visit: 7/21/2025 Posts: 50 Rating:
|
Thanks to all I solved the problem by changing the access level of CPU in TIA portal. |