Dear All, We have used 2 feeder -110VAC primary & secendory UPS Power Supply for Renduncy. But I have used workstation with only one power supply point so is it possible to take 110VAC primary & secendory UPS Power Supply on one busbar & I can take 110VAC to my workstation... Please find attached doc. for your ref. Please reply me
AttachmentPower supply distribution.pdf (509 Downloads) |
|
Rajkiran Patil |
|
| 2/21/2014 3:11 AM | |
|
Posts: 4 Rating:
|
Dear Rajkiran, You can not parallel two UPS outputs, unles they are synchronized. Tharaka
|