(2)| 4/17/2018 4:09 PM | |
|
Joined: 9/27/2005 Last visit: 12/16/2025 Posts: 203 Rating:
|
Hi, there are helpful application examples available, which shows the wiring. For E-Stop: https://support.industry.siemens.com/cs/ww/en/view/21064024 For safety door: https://support.industry.siemens.com/cs/ww/en/view/21063946 Greetings |
This contribution was helpful to
|
|
| 4/18/2018 3:52 PM | |
|
Posts: 35 Rating:
|
Hey Morten, Thank you for the help. i am a little confused when it comes to using Us0, Us1, Us2 and Us3. it looks like Us0 can only be used with one input. (is that correct)? So my question here is, if i use Us0 and DI0 how do i make use of DI1,DI2, and DI3 in that group?? thanks for the help. Sam |
| 4/19/2018 3:40 PM | |
|
Posts: 35 Rating:
|
okay so one last question, this is (see attached) correct ?? Attachment0539_001.pdf (698 Downloads) |
| 4/19/2018 4:52 PM | |
|
Joined: 4/8/2013 Last visit: 3/20/2025 Posts: 72 Rating:
|
If you have four 1-channel sensors that wiring is correct. However, you have a 2-channel emergency stop and two 2-channel protective doors, right? The two sides of your module (a/b) create your pairs. Wire your emergency stop to CH0 and CH8, protective door 1 to CH1 and CH9, protective door 2 to CH2 and CH10. You can see these pairs also in the configuration of your F-DI (see attachment). Because of the two different sensor supplies of each channel, the F-DI is able to detect short-circuits between the two channels. I second Morten's suggested application examples. They are really helpful if you're just getting started with SIMATIC Safety. Also, there is another application example for protective doors without interlocking: |
| 4/25/2018 11:10 PM | |
|
Posts: 35 Rating:
|
Hey Guys, thanks for all the help! attached is how am going to be wiring my SF PLC. let me know if you see something wrong with it. again thanks, Sam |
Follow us on