(0)| 1/26/2009 2:40 PM | |
|
Posts: 1776 Rating:
|
Hi have you checked the WinCC diagnostic files? |
| 1/29/2009 6:53 AM | |
|
Joined: 8/27/2008 Last visit: 5/13/2025 Posts: 57 Rating:
|
Dear April, You mean file generated from "apdiag.exe"? regards, rami |
| 2/1/2009 7:45 PM | |
|
Joined: 8/27/2008 Last visit: 5/13/2025 Posts: 57 Rating:
|
Dear All, attached are the WinCC diagnose files. Today i deleted the complete folder and downloaded again to both OS_serv and OS_serv_stby. Therefore you may concentrate only on error dated 01 feb 2009 (today). The flippering still there even immidiately after WinCC start up (but only when there is data change as explained before) regards, rami AttachmentDiagnose.zip (119 Downloads) |
| 2/3/2009 12:19 PM | |
|
Posts: 993 Rating:
|
Hi, it seems you have communication problems with the S7 see Sys_02.log 255,01.02.2009,13:20:06:399,1000204,4,operator1,PC_SERVER_STBY,DataManager Runtime,S7$ProgramConnection 'S7$Program' disconnected 255,01.02.2009,13:21:09:931,1000205,4,operator1,PC_SERVER_STBY,DataManager Runtime,S7$ProgramConnection 'S7$Program' connected and SIMATIC_S/_Protocol_Suite_01.log 2009-02-01 13:20:06,383 ERROR Connectionerror 1 "S7$Program": Errorcode 0x0000 7001! 2009-02-01 13:20:06,383 ERROR Cannot connect to "S7$Program": Errorcode 0xFFDF 4107! 2009-02-01 13:20:21,711 ERROR Cannot connect to "S7$Program": Errorcode 0xFFDF 410E! Explanation of the errorcode can be find with this FAQ http://support.automation.siemens.com/WW/view/en/16622456 |