Hlo Sir, I am learning programming language. Si want to know logic of FC105 in ladder and STL. Enclosed pic for the reference.
------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 02/07/2024 12:23:55New subject after splitting |
|
| 2/7/2024 1:01 PM | |
|
Joined: 7/9/2015 Last visit: 12/17/2025 Posts: 4493 Rating:
|
Hi, hope this helps: For an S7-1200/S7-1500 controller in STEP 7 (TIA Portal), how do you scale integer values in real numbers and vice versa for analog inputs and outputs?Regards, Towome |
|
|
|
| 2/7/2024 3:35 PM | |
|
Joined: 7/7/2010 Last visit: 12/23/2025 Posts: 16325 Rating:
|
Since Siemens codes the provided SCALE instruction for S7-300/400/1500 PLCs in a closed-source manner, we cannot tell you what the code looks like. We can (and someone kindly already did) provide you with the expected way to scale analog values for S7-1200/1500 using NORM_X to normalize a range of values to 0.0 to 1.0, and then provides SCALE_X to accept the normalized range of values and convert to either user units, engineering units, VFD units, HMI scaling units, and so on. You can have a single NORM_X and provide that normalized output into several SCALE_X blocks to get several scaled values from the same source value. That option can reduce the amount of normalization calculations the PLC is required to do (a bonus) - if multiple scaled outputs are needed.
|
|