which screen? |
1/10/2025 6:52 PM | |
Joined: 5/6/2022 Last visit: 9/9/2025 Posts: 589 Rating:
|
Hi johannes261, It is only possible to upload the program blocks, including the safety program if the CPU is a 1500 with firmware of at least v2.1. Additionally, the "enable consistent upload from F-CPU" must have been selected in the program, before the original program was downloaded to the CPU. Unfortunately, it is not possible to only download the regular blocks from the CPU, as everything in the CPU will need to be uploaded. Therefore, the original project will be required, in order to get the program blocks from the CPU, I have attached the fail-safe manual below for your information, page 92 has information on the requirements for uploading from an F-CPU. Best regards!
|
If this Information really helps, you could use the Rate function |
|