(3)| 11/10/2009 11:32 AM | |
|
Posts: 18 Rating:
|
Hello Sydney Thank you for your response, I wrote the forum thread while pulling out my hair trying to remidy a breakdown. I will try to elaborate as mentioned we hard a hardware failure of a analoge card(6ES7 124 1FA00 0AB0), we had no spare part. Therefore we removed the faulty card and changed the hardware configuration. This removed the fault light from the PLC and ET200L SC, we then hard wired from a different analoge card in the main CPU rack to the existing control loop changed the hardware configuration to set up the new channel on the card and downloaded this configuration. This was all OK. I then located the PQW260 in the programme (this is the address of the orignal analog card) and changed the address to the new analog card). This is when the problems started after changing only network 14 of FB51 OUT62 from PQW260 to PQW368 the block could not be saved and downloaded due to the following error: Network 14 (34:40) Compiler information :type conflict When you click OK it takes you to Network 14 IN16 P#DB12.DBX0.0 As already mentioned if you go online this network is present and active in the programme as it is controlling 3 analog outputs. Therefore I still have a problem that I can not modify the programme to suit my hardware changes. Is there away of reading a PQW value and assigning to a different PQW, instead of trying to change this FB51? I have attached the relevant parts of the programme, any help would be greatly appreciated Kind Regards P. Lovell AttachmentPl_block.zip (282 Downloads) |
| 11/12/2009 12:33 AM | |
|
Joined: 1/4/2008 Last visit: 12/22/2025 Posts: 703 Rating:
|
You're welcome Regards Sydney |