(0)| 11/25/2010 6:09 PM | |
|
Joined: 1/28/2009 Last visit: 12/26/2025 Posts: 6889 Rating:
|
Dear member
Check also this post for a similiar question: Configuration hardware when cpu in run mode |
| 11/26/2010 8:20 PM | |
|
Posts: 22 Rating:
|
hi what about reading data such as order number of modules or type of module used in configuration. thank you |
| 11/26/2010 9:15 PM | |
|
Joined: 9/27/2006 Last visit: 12/26/2025 Posts: 12474 Rating:
|
Hello srv; SFC51, with the dedicated SZL-ID index, can be programmed to collect data from the PLC modules. For an example onreading module information and status, either on a network or in the main racks, have a look at the following FAQ. How do you find out the status of the stations of a DP master system or of a PROFINET IO system? You can find a complete list of SZL-IDs you can request with SFC51 in the Standard and System Functions manual. System Software for S7-300/400 System and Standard Functions Volume 1 and Volume 2 Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 11/26/2010 9:19 PM |
|