Hello AGR it's just the way it is and could possibly be only answered by the Siemens Developers. I can tell you though that the 16 Bytes of I/O that each CP occupies in a 300 is used as the communications channelbetween the CPU and the CP and accessed by the standard communication FC's and FB's for that CP (note that these 16Bytes have nothing to do with the amount of datathat you can send/receive via a CP). Simply give your CP's a higher start address(considering the maximum address that your CPU can have) and then expand the PII and PIQ to suit your needs. I hope this helps |
Cheers |
|
6/25/2012 9:10 AM | |
Joined: 10/7/2005 Last visit: 9/14/2025 Posts: 3049 Rating:
|
Hello AGR I fear I don't really understand your question but can tell you this much: A 300 CP occupiesI/O addresses. These I/O addresses MUST be outside of the CPU's I/O Process Image. These I/O addresses must however (somewhat obviously) fall inside the CPU's overall I/O address area. Example:A 6ES7315-2EH14-0AB0has a max I/O address area of 2048 Bytes. Let's say you set it's I/O Process Image size to 1024. Result: The lowest I/O address you can set for your CP is 1024 and the highest is 2032. I hope this helps |