Hello, see in the manual (link) the description and informations in refer to chappters of PULSEGEN. http://support.automation.siemens.com/WW/view/en/57185407 With best regards |
| 1/28/2013 4:17 PM | |
|
Joined: 1/28/2009 Last visit: 1/5/2026 Posts: 6892 Rating:
|
Hello , If your actuator is only one control valve , triggered with one binary signal to be closed, and with another binary signal for open command, I suggest CONT_S. This function is used for integrating actuators as I explained in the previous paragraph and note, if there is no command actuator stay at its previous opening.For those actuators I can name "Slide Valves" and "Motorized Operated Valves". More information on page 4083 of the following manual: STEP 7 Professional V11.0 SP2 Update for more help! Best regards Hamid Hosseini |