(0)| 12/15/2012 11:06 AM | |
|
Posts: 1 Rating:
|
Hi, how can I add GSDML files to catalog in TIA Portal V10? Thank you in advance for your answer |
| 12/16/2012 12:00 PM | |
|
Posts: 1742 Rating:
|
Hello, When you want to use Profinet IO in combination with S7-1200, you need a v2 CPU and TIA portal V11. With the TIA Portal V10.x it is not possible. Here the link to the manual STEP7 V11 SP2 http://support.automation.siemens.com/WW/view/en/57185407 You will find the procedure below: Requirements
ProcedureTo install a GSDML file, follow these steps:
|
This contribution was helpful to
|
|
| 11/28/2013 9:12 AM | |
|
Joined: 4/24/2009 Last visit: 8/20/2024 Posts: 2682 Rating:
|
New question splitted to S7-1200 GSDML file Best regards O_Moderator |