I can not connect to the PLC ( S71200) on TIA v12. Getting "communication server could not be started" what is this? Can somebody explain the reason. thanks
|
| 6/6/2015 6:53 AM | |
|
Joined: 5/12/2006 Last visit: 12/19/2025 Posts: 22816 Rating:
|
Hello,
check that the Windows Service "Simatic S7DOS Helper" is running.
Christoph |