Default Header
(0)| 7/3/2008 6:25 PM | |
Posts: 1 Rating:
I have two cpu 922 with coordinator 923 and cann't make online with them although they have a problem and i make overall reset and they are run mode now but still gives me plc timeout if i try to make online through any of cpus or coordinator .......i need help plc part no : 6es5 932-2uc11 coordinator 6ES5 922-3UA112 CPU 6ES5-526-3LF11 6ES5624-3UA13 6ES5-513-3MB12 DI /DO/AI/AO MODULES using Laptop with Step 5 V 7.23 programing cables RS232/TTY cable from www.helmholze.com waiting your Help usin |
| 7/3/2008 7:45 PM | |
Posts: 1742 Rating:
Hello, Because you cannot connect with any of the CPUs, the problem must be a common error. From the page http://www.helmholz.de/prod.d,48_56_85.html?prod=68 On the TTY side, the SSW4 uses the current sources of the remote unit, the RS232 side is powered via the RS232 status signals. One possible problem is that the 15V is defective, with as result that the current loops are not powered. On the power supply you have a LED indicating if the 15V is OK or not. |