(2)| 5/9/2018 4:32 AM | |
|
Joined: 10/7/2005 Last visit: 1/9/2026 Posts: 3054 Rating:
|
Hello Msorich while I agree that it is highly likely that the crossed out FC's and FB's are unused "leftover" Blocks that can be safely deleted, allow me to add a word of caution. Blocks can be called indirectly in which case they will still show up with a Cross in the Call structure but are of course called and required for correct program execution. The pic has a "stupid" example of one way of doing so and at least some OEM's have a tendency to "protect" their know how via some clever (and/or convoluted) programming practice. Suggest you do more homework and/or run the program in PLCSIM and delete suspected surplus Blocks there first before doing so in the production machine. |
Last edited by: fritz at: 5/9/2018 4:39:28 AMCheers |
|