Hello nanchi; You do not mention the software (and version) you are using to do this upload. Here are 2 links that can glep you out: - For Simatic Mnanager (Step 7 v5.x) : - For TIA Portal : https://support.industry.siemens.com/cs/ww/en/view/97554052 Where you may have problems is with the Profibus nodes. The ET 200S station is a Siemens product, as such it i hould be part of the Profibus catalog of your software, and should upload easily. If the drives are from a 3rd-party, you may have to look for their gsd file (on the manufacturer's site) and integrate them in the Profibus catalog before the uploaded project could work. Note also that an uploaded program comes without comments or symbols, so it could be a bit difficult to understand the program flow and the functions. If you have electrical drawings of the project, you could use them to attempt to reconstruct the symbol file, at least for the I/Os. Hope this helps, Daniel Chartier |