HI I have upload S7 300 station symbol table is empty. what could be the reason. And wen i open a block flowing error massages. Best Regards Chin |
| 8/19/2018 5:45 PM | |
|
Joined: 9/27/2006 Last visit: 12/26/2025 Posts: 12474 Rating:
|
Hello kcnfer; You are working with an uploaded program from a S7-300 (or S7-400) CPU? The fact that you have no symbol or parameter information is quite normal. Symbols, commets and parameter names are not downloaded to the CPU along with the program blocks after compilation, so they cannot be retrieved, unless you have access to the original program. See the following discussions for more information: symbol data https://support.industry.siemens.com/tf/ww/en/posts/symbol-data/106359/?page=0&pageSize=10 Parameter and local variable names are not available after uploading program Hope this helps, Daniel Chartier |