Hi, It's possible to obtain the LOAD MEMORY (RAM) as a number on the program so i can generate an alarm? Thank you in advance ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 06/19/2020 10:31:26New subject after splitting |
|
| 6/27/2020 10:13 AM | |
|
Joined: 10/7/2005 Last visit: 1/14/2026 Posts: 3054 Rating:
|
Hi alkimux while I haven't had the need to use this particular combination yet, SFC 51 with SSL-ID W#16#0113 should do the trick (assuming S7-300/400 usage as this is posted in the classic Step 7 conference). Truth be told, I'd rather keep an eye on the (non expandable) work memory via this and fit a large enough RAM card for the load memory. |
|