(1)| 4/24/2019 8:28 PM | |
Joined: 9/27/2006 Last visit: 1/14/2026 Posts: 12481 Rating:
Hello Hich_IO; Are you sure? I agree that it might be confusing... - According to the ET 200MP F-DI manual a discrepancy diagnostic alarm will be generated both on short-circuit detection and on wire-break at the sensor (see section 6.3) SIMATIC ET 200MP digital I/O module F-DI 16x24VDC https://support.industry.siemens.com/cs/ww/en/view/109482426 2- In chapter 7, the Technical specs state that there is no support for wire break detection ... It most probably is an error in the manual, but which statement is true? You should bring this ot the attention of Product Support, using a Support request (the link is at the top of this page). We would be very interested in their answer. Hope this helps, Daniel Chartier |
| 4/25/2019 2:40 PM | |
Posts: 10 Rating:
Hi, Thank you for your answer, I sent a ticket to Siemens support to provide me with clarifications regarding this discrepency, Thanks you. Hich_IO |