(2)| 11/14/2013 8:12 AM | |
|
Posts: 378 Rating:
|
Hello, as written in the following entry, you need at least v5.4 SP4 to http://support.automation.siemens.com/WW/view/en/38727042
You have two possiblities now.
Best regards Bilao |
This contribution was helpful to
|
|
| 11/14/2013 8:17 AM | |
|
Joined: 5/28/2008 Last visit: 12/23/2025 Posts: 4522 Rating:
|
Hello, To program this CPU "6ES7315-2EH14-0AB0", You need at leastSTEP7 V 5.5 or higher Please look at second section "Engineering with" in the technical specification of this CPU. To upgrade your software from Step 7 V5.4 to V5.5, you need to buy: "6ES7810-4CC10-0YE5" Another solution: If you are not planning to upgrade your software for now, you can use in HW configuration the elder type; part number "6ES7315-2EH13-0AB0" Thus because the CPU6ES7315-2EH13-0AB0became obsolete and the successor of it is6ES7315-2EH14-0AB0 Please check sucessor tab of the above link of old CPU. Hope this helps. |
|
Ayman Elotaify |
|
This contribution was helpful to
|
|
| 11/18/2013 11:05 AM | |
|
Posts: 25 Rating:
|
U NEED SP4 V 5.4 AND GIVE UPDATE |