(1)| 11/25/2013 11:55 AM | |
|
Posts: 90 Rating:
|
Hi, you can download the manual here: http://support.automation.siemens.com/WW/view/en/1137637 and take a look at chapter 5, page 29
|
Last edited by: O_Moderator at: 11/25/2013 1:03 PMlink corrected |
|
| 11/25/2013 3:06 PM | |
|
Joined: 11/13/2013 Last visit: 6/16/2025 Posts: 11 Rating:
|
hi Ariya Man ! Thanks you for help |
| 11/26/2013 8:41 AM | |
|
Posts: 1121 Rating:
|
Hi Be very carefull in R system as the follwing rule will apply. 1. Do not use more amount of Memory Bits 2. The FC and DB should be in Sequence 3. Do not use S5 timers in the program, Use only IEC timers. Find the attached Documents AttachmentSoftware Redundanz.pdf (384 Downloads) |
This contribution was helpful to
|
|