Hello AllanSoag, Take a look: Protection of Programs on PLC How can you activate the protection level with a password in the HW Config for an S7 CPU? |
Last edited by: Ste39 at: 3/6/2014 5:42 PM |
|
3/6/2014 6:14 PM | |
Joined: 11/14/2013 Last visit: 10/27/2021 Posts: 11 Rating: (0) |
Does this need to be done online to the controller as the fields are greyed out at the moment as I am offline. |
3/6/2014 8:41 PM | |
Joined: 1/28/2009 Last visit: 9/10/2024 Posts: 6849 Rating: (1365)
|
Hello, Changes in Hw.config is done in offline mode.As the fields are in black for S7-300 ,so you need CPU in STOP mode to download the changes.For your problem regarding "fields are greyed out at the moment", You should select the protection level 3 as shown in the attachment.This protect your final project inside PLC for unauthorized access. If it is not your case, please provide some snapshots.For more information, read links provided by "Ste39". I hope it helps. Hamid Hosseini |