(0)| 12/3/2014 7:46 AM | |||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
|
Posts: 5 Rating:
|
The below BOM is a PCS-7 system with redundant IOs. Is this system SIL-1?
--------- new subject after splitting from Is there any guide which components do we need to make SIL1,2 or 3? |
||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
Last edited by: CS Moderator at: 12/3/2014 12:05 PMsplitting |
|||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
| 12/4/2014 4:06 PM | |
|
Joined: 1/15/2009 Last visit: 10/30/2025 Posts: 316 Rating:
|
Hi GDA, The details of what SIL level will not only be determined by the hardware (IO modules and MTAs), but also how they are installed/Configured. Below are the ET-200M manuals for Failsafe IO modules and MTAs. F-IO Manual http://support.automation.siemens.com/WW/view/en/19026151MTA Manual Supported IO Module/MTA/Cable Combinations
|
|
The best location for all PCS 7 content (manuals, guides, application notes, FAQs, and videos). |
|