5/18/2009 1:30 PM | |
Joined: 1/29/2008 Last visit: 7/26/2022 Posts: 419 Rating: (19) |
Hi The problem is that the Siemens SIMATIC S5 PLCs are programmed via a TTY serial interface (called also 20mA Current Loop). To connect a PC, which is normally equiped with RS232 ports, a converter is therefore required. You can try to find one on the internet or you can try to bild you one. I send you one which I found it on a site but it is a passive one. I don't know if it is working but I think that is worth to try it. Good luck Nit Attachment232_20MA.zip (424 Downloads) |
5/18/2009 3:16 PM | |
Posts: 9 Rating: (1) |
Hi Thanks for your reply, My system is a SINUMERIK 840C Controller, with integrated S5 PLC . |
5/18/2009 4:20 PM | |
Joined: 11/25/2005 Last visit: 2/12/2024 Posts: 21 Rating: (0) |
HI, It is possible to communicate with the S5 plc of 840C with a pc equipped of a serial port. Here is the drawing of the cable, kept from Doc on CD 840C ( given for a 25 poles serial port). Regards Attachment6FC9 344-4R.pdf (444 Downloads) |