6/27/2009 12:27 PM | |
Posts: 62 Rating: (0) |
Thank you sir, Will do. I will get back to you and let you know how i got on. Thanks, Raymondk. |
6/27/2009 1:25 PM | |
Joined: 7/2/2008 Last visit: 9/30/2024 Posts: 928 Rating: (309) |
Hello Raymondk, Darius' solution is good. I never did it but I hope it will work. However, If you still like to do it without scripts, you can use this link to learn how to handle change connection between 2 PLCs. It's talking about WinCC flexible with H-System but the core of solution is the same with SWR. Best regards. H-H |
This contribution was helpful to1 thankful Users |
6/29/2009 7:58 PM | |
Joined: 9/28/2005 Last visit: 12/10/2024 Posts: 2957 Rating: (243) |
Hi, I've created simple script for you which compiles, but I didn't tested it. You can test it by yourself. See attachment for details. Attachmentscreen_001.zip (627 Downloads) |
Best regards, |
|
6/30/2009 9:12 AM | |
Joined: 5/8/2006 Last visit: 10/16/2024 Posts: 1085 Rating: (78) |
Hi Your should write the "If ... then" command in the same line, then it should work. Bye |
7/9/2009 12:37 PM | |
Joined: 5/8/2006 Last visit: 10/16/2024 Posts: 1085 Rating: (78) |
Hi 1. Discussion If you want to change your connection back, then you can only set M1000.1=0 in the PLC2 (Connection_4) because you have no connection to PLC 1 (Connection_5). The panel doesn't know the changing of the flag M1000.1 in the PLC1. 2. Discussion You can set your acquisition mode of tag to "cyclic continuous" in the tag editor. The panel gets in each cases thechanging of tag from the plc. It's dependson the acquisition cycle. Link: http://support.automation.siemens.com/WW/view/en/23842653 May this entry will help you, too: http://support.automation.siemens.com/WW/view/en/35538370 Bye |
Last edited by: ZAK at: 7/9/2009 12:38 PMLast edited by: ZAK at: 7/9/2009 12:37 PM |
|