9/17/2010 3:56 PM | |
Posts: 65 Rating: (0) |
hello sir, [schnippschnapp]Another question is related with the image table of analog I/Os. Since s7-300 series controllers does not have Image table for analog I/Os so it is using analog module for memory and bcos of that i am using PIW/PWQ.(PIW256).Is the explaination correct??????? [schnippschnapp] Splitted from Byte allocation for digital and analog I/Os. |
Last edited by: O_Moderator at: 9/20/2010 2:41 PMnew subject after splitting |
|
9/24/2010 3:05 PM | |
Joined: 9/27/2006 Last visit: 12/20/2024 Posts: 12307 Rating: (2695)
|
Hello Oscar; If you do not mind waiting for the OB1 cycle to complete, yes you can access analog values through IW and QW addresses, as part of the process images tables. Just make sure the addresses used are inside the limits of the process image tables for your CPU (see the technical specs). In some CPUs (S7-400) you can even use image partitions (PII), which divide the image tables into sub-tables that can be updated at different cycles. This way your scan cycle is made asynchronous, and predictable. This is used for PCS 7 projects, as I have seen. For more information, have a look at the following FAQ: Where and when do you need peripheral addressing? http://support.automation.siemens.com/WW/view/en/18325417 Hope this helps, Daniel Chartier |
Follow us on