(2)| 11/22/2010 10:59 AM | |
|
Posts: 8092 Rating:
|
Hello everybody, 30 views so far but not a single reply. Is it so difficult? DEEP. |
| 11/26/2010 9:53 AM | |
|
Posts: 8092 Rating:
|
Hello Experts, Ok I will put this in another way. While selecting MCCB which one should be prefered i.e. 25 KA capacity or 50 KA capacity. Regards, DEEP. |
| 12/16/2010 1:14 PM | |
|
Posts: 7 Rating:
|
Dear Deep, |
| 12/20/2010 1:30 PM | |
|
Posts: 8092 Rating:
|
Hi srrr-in, Where shall I get that information. Regards, DEEP |
| 2/11/2011 3:31 PM | |
|
Posts: 66 Rating:
|
Hello Deep, As an example you could check the "Planning Manual - Planning with SIVACON S8, Flexible Low-Voltage Switchboard", available on http://support.automation.siemens.com/WW/view/en/20356391/133300. Chapter 8.10 provides a table showing short-circuit currents of three-phase distribution transformers.These are maximum values on the transformer output. The longer the cable way from the transformer to your panel the lower this value (impedance of the cable). Regards, Sentronix |
Follow us on