Hello. First look at the chapter 9.13 of the manualof 6RA70 drive, where it is described how to set required parameters for USS connection. Then look at function diagram sheets G170-G172, where you will find how to connect setpoints/actual values using connectors. |
1/13/2011 8:21 AM | |
Joined: 8/25/2006 Last visit: 9/25/2024 Posts: 2209 Rating: (278) |
Irecommend to use G-SST2 for USS connection (X172 on CUD1) and G-SST1 leave for OP1S and Drive monitor. If in S7-200 you don't use PKW, then P782=0. P781 should have the number of process data words (how many words S7-200 sends/receive to/from the drive).
As I know DriveMonitor does not support 6RA28. For connecting to 6RA70 use the SIMOREG DC MASTER drive type. And try the latest version of DriveMonitor. |
1/13/2011 3:44 PM | |
Joined: 8/25/2006 Last visit: 9/25/2024 Posts: 2209 Rating: (278) |
May be this was the reason. When you change the parameters P780 to P788 you may change the default settings for Drive Monitor connection. Change this parameters back to the factory settings and try to connect with DriveMonitor to the X300 on the front panel of drive. |