5/23/2011 7:31 PM | |
Joined: 10/22/2008 Last visit: 9/19/2024 Posts: 369 Rating: (5) |
How to wrie script or is it any other way to make graphis change not using PLC tags? I would like to in steps change graph so it looks like fan rotatets. I thought to change value with script by ow to make it run every 500ms? Splitted from Is there a manual about writting scripts in WinCC flex? . |
Last edited by: O_Moderator at: 5/24/2011 8:28 AMnew subject after splitting |
|
5/23/2011 8:19 PM | |
Posts: 8946 Rating: (999) |
This link is very helpfull: http://support.automation.siemens.com/WW/view/en/26165877 |
Last edited by: IBN-Service at: 5/23/2011 8:19 PM |
|
This contribution was helpful to1 thankful Users |
5/25/2011 12:37 PM | |
Posts: 327 Rating: (28) |
Greetings About the fans and animations. You need only one PowerTag for all animations. Use one internal counter for each different fan (counter is used for selecting a graphich in the graphic list) and just change the counter whenever the PowerTag changes. Actually, you need only one counter if all animations have same number of graphics in graphic lists. Something like this: counter = counter + 1 if (counter > max) counter = 0 If you really don't want to use PowerTags, you can check this:https://support.automation.siemens.com/WW/llisapi.dll?func=cslib.csinfo&lang=en&objid=26120986&caller=view Best regards
|
5/27/2011 1:06 PM | |
Joined: 5/13/2008 Last visit: 12/18/2019 Posts: 836 Rating: (71) |
Hi fbelic, in chapter 4 (Download) of this FAQ is an OCX, called"WinCCTrigger.ocx": http://support.automation.siemens.com/WW/view/en/31492549 This offers a trigger sequence of 2 seconds without any tags, but works only on a PC (Flexible RT) not an a panel.. |
mfG / Best regards |
|
This contribution was helpful to1 thankful Users |
8/5/2011 2:33 PM | |
Joined: 10/22/2008 Last visit: 9/19/2024 Posts: 369 Rating: (5) |
Now I understand. Significant is to connect script with cycle tag/bit in PLC. |
8/5/2011 4:00 PM | |
Posts: 327 Rating: (28) |
Greetings Yes. Also, be sure to set the trigger tag to cyclic continous acquisition cycle, with adequate cycle... I always forget Bedt regards
|