Hello, I think your old MP277 wasn't an Failsafe model (no emergency button). With the new one you need a F-PLC. The system reacts as you described if there is no F-PLC. The requirement for F-System in redundant configuration depends on your safety requirements. If you have any safety sensor normal you need a safety actor of safe operation. If it is not needed (the Emergency Button on Panel) you need only the CPU. For Operation you need the PROFSAFE communication and the Function blocks in Safety PLC Program. There is a sample available. Configuration and Use of the Mobile Panel 277F IWLAN With other communication i mean Laptops, Telephones, other data communication not only SCADA communication. There is no need for special switches, but for Wifi Communication in bigger installations IPCF-MC is the only system which can guarantee fast handover times. A regular Wifi system can have high response times and then the safety system will stop the machine. If you don't need safety, then use very high safety times. |