2/11/2016 3:57 PM | |
Joined: 9/27/2006 Last visit: 9/19/2024 Posts: 12282 Rating: (2684) |
Hello S7-Freshman; The following manual clearly states that CiR can only be implemented with S7-400 CPUs:
SIMATIC STEP7 V5.5 Modifying the System during Operation via CiR
https://support.industry.siemens.com/cs/ww/en/view/45531308
Hardware Requirements
You require the following hardware configuration in order to be able to modify the configuration of a system in RUN mode via CiR:
• Implementation of an S7-400 standard-CPU (CPU 412, CPU 414, CPU 416 or CPU 417) as of Firmware V3.1.0 or an S7-400-H CPU (CPU 414-4H or CPU 417-4H) in stand-alone mode as of Firmware V3.1.0
• If you want to make modifications to the system during operation with an external DP master (CP 443-5 extended), your configuration must operate at least with Firmware V5.0.
• If you want to add modules to ET 200M: Implementation of an IM 153-2 as of MLFB 6ES7153-2BA00-0XB0 or IM 153-2FO as of MLFB 6ES7153-2BB00-0XB0. You must furthermore install the ET 200M with active bus elements and provide sufficient space for the planned expansion. You may not implement the ET 200M as DPV0 slave (via GSD file). Hope this helps, Daniel Chartier |
2/11/2016 8:21 PM | |
Joined: 9/27/2006 Last visit: 9/19/2024 Posts: 12282 Rating: (2684) |
Hello S7-Freshman; I do not understand what you mean. You need CiR to add or delete a PA slave over the Profibus network in Runtime. But PDM always enables you to see and check the parameters of all the instruments connected to the Proofinus-PA system. As long as the programming PC (or any PC with PDM installed) has access to the Profibus network you can view the values and status of the instruments (on the PC). You can also generate (and correct) the configuration of the Profibus-PA network using the functions of PDM. See if the following information page can give you more details on PDM communications: Also check the following document explaining CiR functionalities on Profibus-DP/PA: SIMATIC STEP7 V5.5 Modifying the System during Operation via CiR https://support.industry.siemens.com/cs/ww/en/view/45531308
Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 2/11/2016 10:32:35 PMLast edited by: dchartier at: 2/11/2016 10:32:54 PM |
|
This contribution was helpful to1 thankful Users |